Resolution: Fix was doing a processor reset in the SUA2200RMXL3U and swapping the batteries on the 9617 card. Cable and software are in the makerspace in case anyone from VCF runs into the same issue. Martin On 1/14/2024 3:45 PM, Martin A. Flynn wrote:
Using the factory DE-9 cable APC SKU 940-0024E on the UPS pass through port,
Connecting with a Toughbook (real serial port, 2400 bps, 8 data bits, no parity, 1 stop bit, and no flow control).
Ordered CR2032 coin cells on the off chance they are depleted from sitting on the shelf.
Martin
On 1/14/2024 3:36 PM, Jonathan Chapman via vcf-midatlantic wrote:
Be aware you may need a goofy cable. I had to make one up when resetting the management card in my old SmartUPS 1000RM after the original card died.
On Sunday, January 14th, 2024 at 15:25, Martin A. Flynn via vcf-midatlantic<vcf-midatlantic@lists.vcfed.org> wrote:
The AP9617 card does not have a separate serial Interface and the pass-thru serial port on the SUA2200RMXL3U does not respond to the factory defaults....
On 1/14/2024 3:18 PM, Jameel akari via vcf-midatlantic wrote:
I would try to re-configure via the UPS’s serial port first. Default username and password are usually apc / apc .