[vcf-midatlantic] anti-static carpet

Dan Roganti ragooman at gmail.com
Sat Feb 6 07:41:48 EST 2016


FYI,
This is only half of the solution.
Shoes are not conductive when it involves ESD, so
The anti-static carpet only works on one condition  - as they are meant to
provide discharge path, so
1. If you are wearing anti-static boot straps - as in a Lab --- I doubt the
visitors have this
2. wearing ESD conductive shoes ---> again, I doubt the visitors will have
this

You like to have the person discharged before you ever enter the room.
As you don't know how much charge they might have, you can have 100,000ev
without even knowing it.
Even if you had just concrete, they can still be charged coming from some
other part of InfoAge
Especially when they have ordinary carpet elsewhere -- remember the door
knob jolt.
And it's .more. prevalent when the humidity is very low - as in the winter,
or in super cold A/C.
It's nice to have a climate-controlled environment but it's not always
possible[$$$]
As you have a need for all 4 systems, A/C, Heater, Humidifier, and
Dehumidifier.
All combinations in the environment can exist, cold/dry, cold/wet, hot/dry,
or hot/wet.

The quickest way is to build a simple ESD Grounding station at the entrance.
All it takes is,
1. a 1meg ohm resistor -- to slowly bleed off the ESD - no jolts
2. some metal [eg. door knob] that is isolated -- something plastic, eg,
pvc
3. and then wired to earth ground.

Then you don't get the zaps or jolts when touching this to discharge
yourself - as on a typical door knob.
The have some kind of sign, such as, "Keep Computers Safe, Get Rid of
Static, Please Discharge" with an arrow pointing to that.
Dan